Let me help you with the actual HVAC math.
So 4x640 is 2600w
You then mul 2600x3.412 (the real btu factor) and get 8871.2 BTUs
So 8872 is you load BEFORE any fans, dehumidifiers or ANY other heat.
Now ACs… 12000 btu per ton is for the TOTAL work it can do BUT there’sa ratio about 70/30 of sensible work, compared to latent work, sensible work cools your lights, latent work dehumidifies the room (yes you can use an AC alone but there’s details)
So 70% of 12000btu or 1ton is 8400btu of Light cooling Sensible work.
You need a little more than 1ton just for the lights.
I looked at the quest website and the 165 is listed at over 9000 BTUs itself so according to that, anytime the dehumidifier is running. It will need 1 ton of cooling for it in addition to the lights 1 ton.
How we haven’t considered environmental factors like do you have a Refrigeration Panels or do you have drywall and fiberglass and wood framing? Is it old construction? It’s not very airtight. That’s going to add Cooling needs in the hot times as you noted.
If I had the money I’d get a 3ton that does three heads and 3-1ton heads and put two in this room, and one in veg,mom.
You can even miss match the heads and manipulate the work…. For example, you can oversize the heads and if zone is not using Cooling. The other zones will get more so you could put two 1 1/2 ton heads in the flower room and one and a half ton had in your vegroom and even though that adds up to 4 1/2 tons you’re only still have 3 tons of total cooling.
Now that I spent all your money ;-)
Don’t start with 1ton,
Here’s more info